Author: Subject: Bathroom Extractor Switch Wiring
myke pocock

posted on 23/6/17 at 03:40 PM Reply With Quote
Bathroom Extractor Switch Wiring

Knowing what a knowledgeable lot you Locosters are can anyone answer this wiring question. My bathroom has two pull switches, one for the lights and one for the extractor fans. I have bought a pull switch with neon indicator for the fan as the current one is a simple light pull and doesn't have a neon. The wiring colours at present are, Power In = blue, brown, earth, Power Out = grey (with a blue marker tape on), blue, black (with a brown marker tape on) earth. My new switch has In = L1, L2, N and Out = L1, L2 N. (common earth point.) Can someone please advise how I wire it up. Cheers in anticipation.

[Edited on 23/6/17 by myke pocock]

View User's Profile E-Mail User View All Posts By User U2U Member
ReMan

posted on 24/6/17 at 12:53 PM Reply With Quote
I think you have a timed fan?
These need a permanent live as well as a switched live
You have bought a 3 pole isolator
What switch did you have before, just a standard 1or2 pole light pull switch?
How is it wired at the moment?
Are any joined off the with terminals?





www.plusnine.co.uk
∙،°. ˘Ô≈ôﺣ

View User's Profile Visit User's Homepage View All Posts By User U2U Member
myke pocock

posted on 24/6/17 at 02:13 PM Reply With Quote
Hiya ReMan, yes it is a standard light pull at present and the fan is timed. At present it is wired with Com = 2 browns, L1 = black with brown marker and the blue and grey with blue marker are joined with a choc block and earths are joined. (think I may have put down slightly wrong colours in my original post.) Hope this helps and thanks for the reply.
View User's Profile E-Mail User View All Posts By User U2U Member
ReMan

posted on 25/6/17 at 11:38 AM Reply With Quote
Sorry for the very badly drawn diagram.
What you've bought is a 3 pole isolator with neon.
To replicate what you've currently got, assuming the timer is inbuilt or elsewhere and to work the neon, this should do it.
i'm assuming the neon is powered from L1 OUT , =but you'll also need the Neutral too, possibly even on the N OUT terminal rather than the N IN

i.e. discard the chocolate block and join the blues on one side of the switch.
I've left all the earths off these all need connecting together on the earth terminals

I hope this helps.

Usual disclaimers , I'm not a practicing certified domestic electrician
bathe
bathe


[Edited on 25/6/17 by ReMan]





www.plusnine.co.uk
∙،°. ˘Ô≈ôﺣ

View User's Profile Visit User's Homepage View All Posts By User U2U Member
myke pocock

posted on 25/6/17 at 05:46 PM Reply With Quote
Jobs a goodun, thanks very much ReMan.
View User's Profile E-Mail User View All Posts By User U2U Member

New Topic New Poll New Reply


go to top






Website design and SEO by Studio Montage

All content © 2001-16 LocostBuilders. Reproduction prohibited
Opinions expressed in public posts are those of the author and do not necessarily represent
the views of other users or any member of the LocostBuilders team.
Running XMB 1.8 Partagium [© 2002 XMB Group] on Apache under CentOS Linux
Founded, built and operated by ChrisW.