On going Central Heating Problems. Please help!

As some of you will know I've been having real problems with air in my heating system and despite checking the various suggestions already received I am now having to bleed some of the rads virtually every day.

Because this is really pi***** me off I spent a couple of hours exposing the pipes and drawing up a circuit drawing as is.




I have compared this with the circuit given in the Worcester boiler installation instructions (the boiler and controls were new this year but the basic system is probably 25 years old).

The main difference seems to be that the cold feed should be between the boiler and pump (in fact within 150mm of the expansion pipe) whilst mine is actually 7 or 8 metres away on the return side of the hot water cylinder coil.

Would this create all the problems I'm getting?

Unfortunately it's not easy to change the cold feed as the boiler is in a flat roofed kitchen and all the pipes go up into the void between the ceiling and roof.

There is a mains cold water supply nearby if I could somehow utilise that but with such old pipework I'm a bit nervous of a pressurised system.

Any comments / suggestions.

John.

View User's Profile View All Posts By User U2U Member
John P

posted on 19/12/09 at 01:23 PM Reply With Quote
Not sure why the picture doesn't seem to work, is this better?

[img] Central Heating Circuit
Central Heating Circuit
[/img]

View User's Profile View All Posts By User U2U Member
turbodisplay

posted on 19/12/09 at 01:53 PM Reply With Quote
Is the heating circuit expansion tank, actually got water in?
My parents system had air when the ball cock got stuck.
Darren

NOTE:This user is registered as a LocostBuilders trader and may offer commercial services to other users
View User's Profile E-Mail User Visit User's Homepage View All Posts By User U2U Member
t16turbotone

posted on 19/12/09 at 02:07 PM Reply With Quote
is the vent an 'auto' type or thumb screw type?
View User's Profile View All Posts By User U2U Member
rachaeljf

posted on 19/12/09 at 02:08 PM Reply With Quote
Looks like the head loss in that 7 or 8 m of pipe is enough for the water level in the overflow pipe to be drawn down so that air is being sucked in where the overflow pipe joins the circuit.

You can try throttling your pump down a bit, or raising the header tank level, or re-routing the cold feed so it comes in nearer to where the overflow pipe joins.

Cheers R

View User's Profile View All Posts By User U2U Member
Bigheppy

posted on 19/12/09 at 05:08 PM Reply With Quote
The short answer is yes it could cause your problems. Previously you were advised that the hot water coil could be cracked, if this was true the header tank which is higest would fill the other tank, If both tanks are at the same level it is often difficult to diagnose. If they are at different levels the lowest would overflow. The cold feed should be connected to the flow pipe ,the one taking hot water away from the boiler, nearest to the pump with the return connected as close as possible to this pipe. This arrangement puts almost equal pressures on both pipes so helps to stop the pump pumping water into the header tank and aerating the water, and/or sucking air into the system. Raising the header tank may help but it probably wont stop any pumping over which aerates the water, this aeration then enters the system and the disolved air contributes to further corrosion of the radiators as well as causing air locks. A temporary fix would be to connect the cold feed into the expansion pipe below the header tank and fitting a vent to the original cold feed point on the system, this does not always work. Another fix would be to increase the volume of the expansion pipe, using en elephant tube! these used to be made fron 11/2" copper tube and dependant on how much vertical space is available up to 1m long. This would be fitted in the expansion pipe just below the tank. In the absence of a tube this size a series of tubes coule be used, drain the header tank and cut the expansion pipe then add several tee's with pipes running parallel to the original then join all these together and vent into the tank as was original. The system should be balanced, first with the system off if you have a gate valve fitted to the flow or return pipe to the cylinder turn all the way off counting how many turns, then open it to half way. Close the bypass and open it up half a turn. Check which radiator heats up the fastest then using the rad valve turn it almost off, then turn the next hottest rad on a little more increasing the amount its turned on until all rads are heating up at the same rate. There types of fixes may work but not having seen your installation I can give no guarantees.

[Edited on 19/12/09 by Bigheppy]

View User's Profile View All Posts By User U2U Member
Ferg

posted on 19/12/09 at 07:14 PM Reply With Quote
I'd agree with the reply above. The vent and cold feed MUST be close together or pumping over is VERY likely. Also as mentioned above, is that vent an auto vent? If so shut it manually, they are rubbish things.
The only other possible solution is to do away with the cold feed on the return and plumb the existing vent into a 22mm tank connector to form a combined cold feed & vent. This was pioneered by Baxi for low head systems in the early 80s. BE WARNED though, that it isn't acceptable unless the boiler has a MANUAL reset hi-limit overheat thermostat.

View User's Profile View All Posts By User U2U Member
MkIndy7

posted on 19/12/09 at 07:46 PM Reply With Quote
If your going to the trouble of altering pipework it might be as well to change it to a pressurised system.

You could then cap off the cold fill and vent and remove the heating header tank.

But you would need to install on the pipework an approx:
20L expansion vessel
A filling loop kit with pressure guage
A 3bar safety valve (vented to outside or a visable drain)

Then once the air is out you should never have the problem again.

View User's Profile E-Mail User View All Posts By User U2U Member

New Topic New Poll New Reply


go to top






Website design and SEO by Studio Montage

All content © 2001-16 LocostBuilders. Reproduction prohibited
Opinions expressed in public posts are those of the author and do not necessarily represent
the views of other users or any member of the LocostBuilders team.
Running XMB 1.8 Partagium [© 2002 XMB Group] on Apache under CentOS Linux
Founded, built and operated by ChrisW.